Seems IW_PR_Schrittnummer is only referenced in 3 spots... where it's declared and where its read in the fbd routine... I guess what I'm asking is something writing a number to this variable... or what? If so how would I find it... also what is the action being performed by this first function block? looks like there are 4 inputs, Auto, is Auto Active, does tasknumber = 0, and is Press Free. if all 4 of these are true... then End Auto. Does that sound right??? someone else programmed this for a job that does work. The tags are in German.
1 Answers
The IW_PR_Schrittnummer
is linked to input I/O using AT %ID716
command. So it gets its value from I/O memory. That basically means that "take this value from input memory at address 716 and the size is D (double word, 32 bits).
I'm not sure how you can check what is in that address when it's defined with direct addressing like this. Hopefully someone else knows a good tip for this!
More info about addresses: https://infosys.beckhoff.com/english.php?content=../content/1033/tc3_plc_intro/18014401038842507.html&id=6547931155168793261
More info about addresses: https://help.codesys.com/webapp/_cds_at_declaration;product=codesys;version=3.5.15.0
That logic from your 1st image works as you said. So AutoFinde
will be TRUE, if Auto
, AutoAktiv
, IstFrei
are all TRUE and the input IW_PR_Schrittnummer
is 0. Otherwise the AutoFinde
will always be FALSE.