Helix Steel's site claims that the small wires (twisted steel micro rebar) they created are a good replacement to a typical rebar concrete reinforcement if not even better.

a reinforcement technology that could product provide quantifiably better resiliency, ductility and elasticity to concrete structures.

It's hard to believe that the small wires could replace long continuous rebars. Their product have been around since 2003 and if that's true what they claim how come I still mostly see the typical long reinforcement bars used on the construction sites? Shouldn't this be mostly used everywhere by now? It doesn't seem to be more expensive and also it is less labor demanding.

2 layers of reinforcement is shown torn up and 1 layer of reinforcement and 50 lbs per cubic yard of Helix 5-25 is shown as barely being cracked

Laurel
  • 30,040
  • 9
  • 132
  • 118
Grasper
  • 3,315
  • 2
  • 22
  • 34
  • Further article on the subject: https://www.concreteconstruction.net/how-to/materials/how-to-use-steel-fibers-in-concrete_o . This is from a concrete industry publication, so perhaps read it skeptically. It claims projects using this type of material since the 1960s and cites a variety of pros/cons. – StayOnTarget Mar 30 '19 at 01:13
  • 1
    This should have been immediately closed as a subjective opinion, and edited to a more objective question. "Better" is not an objective term, unless you specify the criteria by which it is to be judged. – Oddthinking Sep 12 '21 at 04:29

4 Answers4

36

The question headline seems to be slightly misinterpreting the company's claims

Carefully rereading their claims, I realized they do not specify what Twisted Steel Micro Reinforcement (TSMR) reinforced concrete is better than. On a quick read, I just assumed they meant it is better than rebar reinforced concrete, because that is what the pictures imply, but it is never explicitly stated.

Helix Steel’s TSMR increases concrete’s strength and resilience and eliminates or reduces traditional reinforcement (rebar and mesh) required by building codes.

This sentence implies that traditional rebar reinforcement is still required in some cases; TSMR is not better than just rebar in all cases.

Helix's Science

Their publications page presents 3 conference papers, two technical reports, and an industry magazine article. I have skimmed through these and found experimental comparisons between plain concrete (not reinforced) and the twisted helix reinforced concrete. I could only find one comparison between rebar reinforced concrete and the helix reinforced concrete, and that related to the explosive test that their pictures show. No quantitative results were presented from that test, just the pictures.

It is worth noting that their best evidence is published as conference papers, which typically face a lower standard of peer review than journal articles. This is definitely a better standard of evidence than I see from many marketing teams, but it isn't the highest standard of evidence.

It is worth noting that helix's product can be used in things like road pavement, where rebar reinforcement is not an option. It can also be used in combination with traditional rebar reinforcement.

Conclusion

From their evidence and a careful read of their claims, TSMR reinforced concrete is definitely stronger than plain concrete. If it is combined with traditional rebar, it can be stronger than rebar alone. Helix does not claim that it will ever replace traditional rebar completely.

BobTheAverage
  • 11,961
  • 6
  • 43
  • 54
  • 2
    Literally: *show me the codze* that state TSMR is acceptable to use in lieu of rebar. Even if it does, it still leaves you open to liability if you decide to use a product from 2003 instead of a proven one from the 15th century. – Mazura Mar 30 '19 at 01:10
  • 1
    @Mazura FYI, rebar reinforced _concrete_ only started to show up in the 19th century. Rebar reinforcement was being used in other ways from 15th century onwards; but using it in concrete didn't begin until later. – JMac Apr 01 '19 at 16:09
10

This is just a form of steel fibre reinforced concrete (SFRC) with twisted fibers. SFRC in general has been around since 1874. It's also been heavily research for at least 50 years (previous source and the last in this answer say this.)

Twisted fibers are slightly better than other kinds in some respects, but not by much. (There's no point in getting into details on this here.)

As for replacing rebar, a more introductory 2018 academic presentation, which is aware of twisted fibers (has photos among the showcased types), has these general points about SFRC in general:

  • The addition of fibres enhances the structural performance of plain concrete (much higher fracture energy)
  • Fibres reduce the crack spacing and crack width, thereby improving serviceability and durability
  • Currently used SFRC mixes exhibit a softening behaviour in tension and cannot fully replace conventional reinforcement
  • Hybrid reinforcement (fibres and conventional reinforcing bars) can be used, but may affect ductility

So, SFRC is clearly not a replacement for rebar in general. And these bits are also relevant:

Several causes are preventing a more widespread use of SFRC:

  • Lack of standardised design procedures and material test procedures

  • High fibre contents (e.g. 1.5% = 120 kg/m3) as required for structural applications (and used in many experiments) are causing severe problems in terms of mixing and workability of concrete mix

  • With common fibre contents (e.g. 0.5% = 40 kg/m3), the tensile strength of concrete cannot be matched at cracking

Since this is written by a (Swiss) professor (ETH Zürich) in this field, I'd be amazed if he hadn't hear of some amazing breakthrough in this respect (in particular for products already commercialized.)

And if that's not enough, he repeats again:

For general application in engineering practice, it is necessary to include conventional reinforcement in combination with SFRC to ensure structural safety and an adequate crack distribution.

As for the table in Dave's answer, which is for a certain application (footings) it comes with this preamble:

For residential footings the International Residential Code (IRC-2015) section R403 describes the use of plain concrete footings provided that the concrete will be in compression. However, it is customary to provide reinforcement to minimize cracking and hold tight any cracks that occur due to drying shrinkage and/or differential temperature effects.

It's only in this optional role that they provide a replacement table. This actually not too surprising. The ETH presentation does mention (and has some pictures) of bridge deck overlays done with SFRC variants; it has a photo (and schematic) example of the Viaduc de Chillon (a bridge in Switzerland).

enter image description here

The same presentation does have one example of "more structural" SFRC-based bridge girders from Dura (a Malaysian company). These do indeed do away with most conventional reinforcements, according to the manufacturer:

DURA® UBG eliminate the used of conventional steel reinforcing bars and stirrups, except at regions where jointing detail are required for composite construction. All steel fibers used are made from high carbon steel wires with tensile strength of minimum 2300 MPa.

Due to the absence of conventional steel reinforcements, DURA® girders can be designed and produced in much slenderer and efficient sections, with no concern for classical issues such as minimum concrete cover, to prevent corrosion of steel reinforcement;

And they have been used in practice:

3rd December 2010 marks the history calendar of engineering in Malaysia as it is the date of the launching of Malaysia’s first ever Ultra-High Performance ‘ductile’ Concrete (UHPdC) bridge girder. This record breaking 50 m single span motorway bridge girder produced and designed by Dura Technology S/B and Perunding Faisal, Abraham dan Augustin S/B holds the marvel of engineering. To date, this bridge girder is considered as the world longest single-span prestressed UHPdC bridge girder for motorway application. The previous record was at 48 m in Japan.

The girders look like this:

(The rebar sticking out is for the aforementioned "jointing detail".)

enter image description here

They have a schematic where this joniting rebar is present and where not (alas it's low resolution):

enter image description here

Fizz
  • 57,051
  • 18
  • 175
  • 291
  • 1
    "High fibre contents (e.g. 1.5% = 120 kg/m3) as required for structural applications (and used in many experiments) are causing severe problems in terms of mixing and workability of concrete mix would" add to the cost of laying a lot and the total cost. – user2617804 Mar 31 '19 at 02:30
  • Unit conversion: the second blockquote discusses a "high" SFRC content of 120 kg/m^3 and a "typical" SFRC content of 40 kg/m^3; the 50 lb/yd^3 in the Helix photo is equal to 30 kg/m^3. – hobbs Sep 20 '21 at 20:47
4

Disclosure - I currently work for Helix Steel.

I think the original question of 'better' is a little vague, and should be "can small wires replace long continuous rebar?" The answer is yes, it CAN, but not always. It depends on what reason the structural engineer spec'd the rebar in the first place. For slabs on ground, footings, precast, some vertical applications, duct banks, etc - yes, Helix can replace most of if not all the rebar, and there is third party verification of that. There are also many situations where a hybrid approach works very well - for example in an ICF home with walls beyond 10' tall where the vertical rebar remains but the horizontals are replaced by Helix.

Here are the links to two independent evaluation reports, UES 279 and ICC ESR 3949, specifying that Helix can be used to replace rebar in certain structural applications under the requirements set forth in ACI 318. ACI 318 lays out actual building code requirements, whereas many other ACI committees provide 'design guidelines' that don't have the same technical constraints.

For suspended applications, certain seismic zone vertical applications, post tensioning, or anything else not specifically covered by those two reports, Helix can not be used.

HelixRep
  • 41
  • 3
  • 4
    Based on your username, I'm guessing you work for Helix? If so, you'd need to disclose your affiliation in your answer. It does appear that the sources you provided are third party so that should be fine. – LShaver Mar 15 '22 at 02:56
  • 1
    Disclosure added to the first line. Hopefully any accusations of 'bias' would apply only to the content of the post, which I'm trying to only use verifiable facts to answer, educate, or clarify – HelixRep Mar 15 '22 at 15:17
  • I saw this used in driveways. Is it a good idea to only use the fibers in a typical residential driveway where the small car traffic is expected? – Grasper Mar 16 '22 at 15:03
  • Helix is used to replace both mesh and rebar in driveways, and is especially useful in situations where the loads are heavier than just cars (RVs, Boat Trailers, etc). Just make sure the contractor follows standard finishing practices (bull float is important here) and only makes one pass with the broom. Standard spacing for joint cutting, unless an increased thickness or dose of Helix is used. – HelixRep Mar 17 '22 at 16:38
-3

Helix is just another steel fiber with a good marketing scheme that dupes most people. There is no such thing as micro rebar and all their claims of being ACI certified are fake. ACI does not certify products... if you don't believe me, here are their certification programs. What the company presents as design methods contradicts with what is presented by ACI 544, which is the expert committee on fiber. Twisted fiber does not test better than other fiber. The Helix 5-25 is 1-inch fiber that actually does not test well from what I've seen. Fibers with hooks sold by Bekaert are much better.

inund8
  • 591
  • 4
  • 20
Mak S
  • 7
  • 8
    [Welcome to Skeptics!](http://meta.skeptics.stackexchange.com/questions/1505/welcome-to-new-users) Please [provide some references](http://meta.skeptics.stackexchange.com/q/5) to support your claims. It isn't enough to say "Do your own research." Please bring the results of the research here. – Oddthinking Sep 12 '21 at 04:27
  • @Oddthinking while not as well written as the other answers, Mak S does direct readers to the codes written by ACI 544 subcomittee. These must be purchased so he can't just link them. It would beneficial to reference proof that twisted fiber doesn't test well, and perhaps quote the relevant sections for ACI 544 that he claims contradicts Helix's claims. I did edit the answer to link to ACI's cert programs. Very little work is needed to improve this answer in my opinion. – inund8 Sep 15 '21 at 19:13